Welcome Guest, Please Login or Register!
Register Search Today's Posts Mark Forums Read Support RL
Home Forum Aquarium Log Gallery Sponsors RHO Bookstore

Re: Gfi

Go Back   Reeflands Forum > Equipment > DIY
Sponsored Links
Reply
 
LinkBack Thread Tools Display Modes
Old 11-12-2005, 08:09 PM   #1
Tenant
 
Join Date: Oct 2005
Location: Ohio
Posts: 91
Re: Gfi

I installed several outlets above my sump that has ben plumbed to the basment. I decided to run my tank on its own breaker, rather than buying GFI outlets I bought a GFI breaker for this purpose. The problem is when conected in the breaker box it won't go to the on postion. It'd dosn't trip just won't turn on. Anyone try these type of breakers?

Thanks
Randy1 is offline   Reply With Quote
Sponsored Links

Old 11-12-2005, 08:34 PM   #2
Contributing Member
 
ibjmg's Avatar
 
Join Date: Feb 2005
Location: fremont ,CA "NOR CAL"
Posts: 155
Quote:
Originally Posted by Randy1
I installed several outlets above my sump that has ben plumbed to the basment. I decided to run my tank on its own breaker, rather than buying GFI outlets I bought a GFI breaker for this purpose. The problem is when conected in the breaker box it won't go to the on postion. It'd dosn't trip just won't turn on. Anyone try these type of breakers?

Thanks

did you try to take the breaker out and switch it to on? could be bad breaker.
ibjmg is offline   Reply With Quote
Old 11-13-2005, 09:01 AM   #3
Tenant
 
Join Date: Oct 2005
Location: Ohio
Posts: 91
Gfi

Yes, It works fine until the power is on. I spoke with an elctrician friend and he says it seems to be installed correctly. I however, don't have a real ground on the box (you know the copper rod in the ground.) I might try installing one and see if thats what the GFI is detecting.
Randy1 is offline   Reply With Quote
Old 11-13-2005, 11:04 AM   #4
Moderator
 
scubadude's Avatar
 
Join Date: Nov 2000
Location: Wichita, Kansas
Posts: 5,293
Quote:
Originally Posted by Randy1
I however, don't have a real ground on the box (you know the copper rod in the ground.) I might try installing one and see if thats what the GFI is detecting.
how do you have the circuit grounded then? I think this IS your problem
__________________
Rocky

scubadude is offline   Reply With Quote
Old 11-13-2005, 12:15 PM   #5
Contributing Member
 
ibjmg's Avatar
 
Join Date: Feb 2005
Location: fremont ,CA "NOR CAL"
Posts: 155
Quote:
Originally Posted by scubadude
how do you have the circuit grounded then? I think this IS your problem


I agree.
ibjmg is offline   Reply With Quote
Old 11-13-2005, 05:14 PM   #6
Tenant
 
Join Date: Oct 2005
Location: Ohio
Posts: 91
Re: Gfi

Well, it has the common ground (White wire) but no ground to the box, I guess that means the whole house isn't really grounded. I'll install the rod and conect to the bus bar in my box then try it. It's probobly good I'm discovering this.
Randy1 is offline   Reply With Quote
Old 11-20-2005, 02:13 PM   #7
New in Town
 
Join Date: Nov 2005
Location: Florida
Posts: 2
Send a message via Yahoo to ReefBum
Exclamation

Installing a GFI breaker

Take a look at the inside of your breaker panel and see if there are 2 differant sets of buss bars. One bar should be for all the ground wires and one bar will be for all your white nutral wires.
If you do not have differant isolated bars for neutral and ground the GFI breaker will not work for you. You will need to go to 1 GFI outlet and then run the other normal outlets off the load side of that. Running the other outlets from the load side of the GFI will protect all the other outlets.

From the problem you describe it is acting just like it would if the grounding and neutral wire were on the same bar or on differant bars that were not isolated from each other. If your home is an older one this is often the case.



Explanation why:

The reason you need differant isolated bars is that a GFI Breaker works by detecting voltage to ground. When you power up somthing from the outlet, voltage comes in from your hot (black) wire and returns via the neutral (white) wire. If the neutral and ground wire at the panel are not seperate then the breaker will detect the returning voltage and trip. Or in your case will not even power on.
This is a simplified way GFI works but I am sure you get the picture.

ReefBum

Electrical/Mechanical Engineer
ReefBum is offline   Reply With Quote
Old 11-20-2005, 04:51 PM   #8
Tenant
 
Join Date: Oct 2005
Location: Ohio
Posts: 91
Thank You so much for your advise.
Randy1 is offline   Reply With Quote
Old 11-21-2005, 09:45 PM   #9
Governor
 
BubbaWPB's Avatar
 
Join Date: Sep 2005
Location: Clearwater, FL
Posts: 1,234
What he said:

Quote:
Originally Posted by ReefBum
Installing a GFI breaker

Take a look at the inside of your breaker panel and see if there are 2 differant sets of buss bars. One bar should be for all the ground wires and one bar will be for all your white nutral wires.
If you do not have differant isolated bars for neutral and ground the GFI breaker will not work for you. You will need to go to 1 GFI outlet and then run the other normal outlets off the load side of that. Running the other outlets from the load side of the GFI will protect all the other outlets....

The reason you need differant isolated bars is that a GFI Breaker works by detecting voltage to ground. When you power up somthing from the outlet, voltage comes in from your hot (black) wire and returns via the neutral (white) wire. If the neutral and ground wire at the panel are not seperate then the breaker will detect the returning voltage and trip. Or in your case will not even power on.
What Bubba heard:
Quote:
blah blah blah blah blah blah blah blah blah. It won't work, dude. (Note to self: learn something about A/C electrical systems soon.)
__________________
Bubba
Hmmm... now that the tank is full, I could convert the pool to saltwater...
Bubba's Aquarium Log
BubbaWPB is offline   Reply With Quote
Old 11-21-2005, 10:34 PM   #10
Tenant
 
Join Date: Oct 2005
Location: Ohio
Posts: 91
Re: Gfi

Why won;t it work DUDE!
Randy1 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are On


All times are GMT -4. The time now is 11:29 PM.



Powered by vBulletin® Version 3.7.0 Release Candidate 3
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0 ©2007, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78