You'll want to use at least two separate circuits, and hopefully circuits that aren't controlled by a wall switch.
Most homes have outlets that are wired with 12/2 and 14/2 wiring. 12/2 can accomodate 20amps (20amps x 120volts = 2400volt-amps) and 14/2 15amps (15a x 120v = 1800va). However, you'll find 99% of the receptacles are only 15a variety, and switched circuits have a capacity of 80% of total. And all the circuits are limited by the circuit breaker that controls the circuit. 20a receptacles look different--one blade isn't a slot, it's a "T" turned on it's side, indicating a 20A receptacle. Even so, a 20A receptacle needs it's own dedicated circuit, otherwise it simply shares with other outlets and lights etc and you'll never get 20A out of it. I've seen 20A receptacles installed with 14/2 wiring (dangerous, only a 15a capacity) on to 20A breakers (FIRE!) or on 15A breakers (breaker will trip way sooner than 20A).
Some wall switches designed for lighting control are derated by 20% to 80% of the circuit's capacity. So, a 15A circuit gets derated to 80% or 12A. the only way to know is to turn the power off the the service panel, remove the switch from the wall, and read the info on the back of the unit. It may be 12A or 15A.
So, on the circuit that you're talking about, you'll have a maximum of 1800v-a to work with. To simplify, let's just call one volt-amp to be equivalent to 1 watt. 1800watts is a good amount of juice, however, it can get used up quick. It's usually unwise to run a circuit at flat-out maximum as conductors will heat up and drop the line voltage lower than 120v. And, if you add something additional, let's say you need to vaccuum, or a table lamp, work lamp, etc, temporarily, you may just trip your breaker. Or your circuit may work fine flat out for weeks/months, only for you to come home and find your tank is dark as the circuit breaker just gave up. (Federal Pacific service panels are crap and will cause you grief).
Anyway, look at all of the labels on your electrical stuff. There should be a rating in V-A (volt-amps) or W (watts). Fluorescent bulbs rated at 40W consume about 65-80W or more, so look for the rating on the equipment. YOur MH lighting is efficient, but a 2x250W is probably consuming 700W continuous, more at strike time. Your pump is probably 200-300W, and the heater is let's say 100W. That's already 1000W.
You should have a GFCI outlet on all of your aquarium stuff to prevent shock and for equipment protection. A tiny shock of 0.005A can kill a human by stopping the heart. If you don't have them, get an eletrician or a competent friend to install them for you. THey're inexpensive ($8 ). And saltwater really conducts eletricity!
------------------