New pendant tripping GFI

Is Perry still around here?

My brand new Sunlight Supply pendant is causing my gfi to trip. Its wired into an electrical box, fired by Sun Aquatics electronic ballasts. I tried switching wiring to other ballast, bulbs, etc. The only common factor is the pendant itself.
__________________
Doug
Papa Doug is offline   Reply With Quote
Sponsored Links

Old 06-04-2006, 01:26 PM   #2
Just Moved In
 
Join Date: Apr 2006
Location: MN
Posts: 35
Open the pendant and inspect the wiring.

Matt
Rubisco is offline   Reply With Quote
Old 06-05-2006, 09:33 AM   #3
Keeper of Willis
 
charlie's Avatar
 
Join Date: Jul 2004
Location: NW Montana
Posts: 6,345
Quote:
Originally Posted by Rubisco
Open the pendant and inspect the wiring.

Matt
It definitly sounds like they have something hosed in the existing wiring in the pendant. See if you can get ahold of the company that sold it to you. Maybe they can talk you thru the wiring while you have the pendant opened up.
__________________
400 Gallon Reef Log
Rome wasn't built in a day---neither is a reef
charlie is offline   Reply With Quote
Old 06-05-2006, 10:02 AM   #4
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
It now appears the pendant itself is fine. I hooked it up separate yesterday to an Icecap ballast I have and it ran fine, although it would not do that the day before on the other ballast and using the GFI plug.

I then plugged the second light in and the GFI tripped again. So my old pendant runs fine on the GFI, the new one does not on the other ballasts but does on an Icecap. The both together trip the circuit but run fine on separate circuits. :slap:

Looks like the GFI may be defective, at least for a pair of 175w halides or a combination of all of the above.
__________________
Doug
Papa Doug is offline   Reply With Quote
Old 06-05-2006, 10:06 AM   #5
Keeper of Willis
 
charlie's Avatar
 
Join Date: Jul 2004
Location: NW Montana
Posts: 6,345
Well............... If you have enuf circuits, sounds like you are gonna be OK, huh? I would look into maybe changing out the gfi, and see what happens. Is that what you were thinking?
__________________
400 Gallon Reef Log
Rome wasn't built in a day---neither is a reef
charlie is offline   Reply With Quote
Old 06-05-2006, 07:29 PM   #6
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
Its been running all day Charlie. I have an extension cord running out into the living room. My wife is really impressed.

So the GFI is faulty, but only when these pendants are running on it. I ran other equipment on it fine.

I have an electrician coming to install a separate breaker and new line for the aquarium, in my wifes brand new modular.
__________________
Doug
Papa Doug is offline   Reply With Quote
Old 06-05-2006, 08:40 PM   #7
Keeper of Willis
 
charlie's Avatar
 
Join Date: Jul 2004
Location: NW Montana
Posts: 6,345
I would definitly have the guy check it before he changes it out, just to make sure tho Doug.
I bet your wife was just thrilled with the extension cord!!!!
__________________
400 Gallon Reef Log
Rome wasn't built in a day---neither is a reef
charlie is offline   Reply With Quote
Old 06-05-2006, 10:36 PM   #8
Tenant
 
captain Jim's Avatar
 
Join Date: May 2006
Location: Ohio
Posts: 57
I had a simmilar problem an took it apart and found a wire was bare and just touching the side, better check just to make sure!
__________________
The pure and simple truth is rarely pure and never simple!
captain Jim is offline   Reply With Quote
Old 06-06-2006, 10:00 AM   #9
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
Quote:
Originally Posted by charlie
I would definitly have the guy check it before he changes it out, just to make sure tho Doug.
I bet your wife was just thrilled with the extension cord!!!!
I need an additonal circuit anyways. My spare room/hide away/office/fishroom, is wired on GFI/arc fault breakers. Ok for some things but not good for firing halides.
__________________
Doug

Last edited by Papa Doug; 06-06-2006 at 02:51 PM.
Papa Doug is offline   Reply With Quote
Old 06-06-2006, 10:02 AM   #10
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
Quote:
Originally Posted by captain Jim
I had a simmilar problem an took it apart and found a wire was bare and just touching the side, better check just to make sure!
I may do that.
__________________
Doug
Papa Doug is offline   Reply With Quote
Old 06-06-2006, 01:15 PM   #11
Just Moved In
 
Join Date: Apr 2006
Location: MN
Posts: 35
Quote:
Originally Posted by Papa Doug
I need an additonal circuit anyways. My spare room/hide away/office/fishroom, is wired on GFI/ground fault breakers. Ok for some things but not good for firing halides.
Just out of curiosity, why would a GFI breaker be bad for metal halide?

Matt
Rubisco is offline   Reply With Quote
Old 06-06-2006, 01:18 PM   #12
Just Moved In
 
Join Date: Apr 2006
Location: MN
Posts: 35
Just out of curiosity why would your GFI breaker be bad for firing your metal halide?

Matt
Rubisco is offline   Reply With Quote
Old 06-06-2006, 02:52 PM   #13
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
Quote:
Originally Posted by Rubisco
Just out of curiosity why would your GFI breaker be bad for firing your metal halide?
Matt
Sorry, I edited my post. It was supposed to read GFI/arc fault breaker. With halides using an arc when starting, it trips the breaker. As does pulling a plug and getting that little spark.
__________________
Doug
Papa Doug is offline   Reply With Quote
Old 06-06-2006, 05:59 PM   #14
Just Moved In
 
Join Date: Apr 2006
Location: MN
Posts: 35
Im sorry, but it is my understanding that with MH all that is needed to ignite the lamp is open current since the ingnition chip is in the lamp itself and not at the ballast like an HPS. Am I missing something here?


Matt
Rubisco is offline   Reply With Quote
Old 06-06-2006, 07:32 PM   #15
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
I dont know. Does the lamp not arc inside when firing? I think it does but never looked close enough. I can tell you that when any of my halides fire, they trip out the arc fault breaker. I also found the same comments on some older arc fault breaker threads on another board.

By the way, this is a separate event from my pendant/GFi breaker problem. The GFI/arc fault breakers are in the electrical panel for the room. The GFI in question is installed in my cabinet and runs off a separate circuit. {the extension cord to the living room, }
__________________
Doug

Last edited by Papa Doug; 06-06-2006 at 07:36 PM.
Papa Doug is offline   Reply With Quote
Old 06-14-2006, 11:08 PM   #16
Governor
 
vtec si's Avatar
 
Join Date: Feb 2001
Location: Denver co, USA
Posts: 1,017
Doug is this on a 15amp or 20amp circuit? I had a simular problem until I added a GFCI breaker to the main panel for that 15amp circuit. Then I was able to take out the 15amp GFI outlet. All my other circuits are 20amp set up the same way. But in your case it sound like something is causing it to short out and make the GFI trip.

I wish I could be more help!
Martin
__________________
VTEC SI
vtec si is offline   Reply With Quote
Old 06-15-2006, 10:52 AM   #17
Gallery Team
 
Papa Doug's Avatar
 
Join Date: Mar 2000
Location: Manitoba, Canada
Posts: 844
Hi Martin,

Been running fine on the extension into the living room so far. Its a 15 amp circuit. I have not tried it on the GFI since then, although I still have other items on it.

The only trip was the GFI recepticle itself and not the panel circuit breaker. However when I tried to run the halides on the rooms circuit, which is on a GFI/AFI in the panel, the halides did trip it. Thats where the halide arc came into effect I guess.

When I run another line, I will install a separate 15 amp GFI breaker in the panel for it.
__________________
Doug
Papa Doug is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
LOA Fixture as HQI Pendant Reef Man DIY 1 03-26-2002 01:18 AM
Halide Pendant ? FISHme Lighting 3 03-18-2002 01:52 AM
HQI pendant w/ NEWBULB 10k newreefman1 For Sale or Trade Zone 1 11-08-2001 02:45 AM
Looking for a MH Horizontal Pendant Aframomum For Sale or Trade Zone 1 09-05-2001 09:18 PM
Does Anyone Have Pendant MH Photos? Reinhold Reef Aquariums 3 06-12-2001 11:34 PM


All times are GMT -4. The time now is 03:23 AM.



Powered by vBulletin® Version 3.7.0 Release Candidate 3
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0 ©2007, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82